concerning 300/500V cables complying to IEC 60227-4, installed in 3phase system 230/400V, I know that it is acceptable to be installed as per  IEC 62440-2008 table 2.(which allows it for up to 320/550V system).

Actually my question is related grouped circuits in same cable tray, conduit , trunking or even panel boards enclosure, rather than the cable it self if it withstand the rated voltage. 

Section 521.6 of BS 7671, states that  " Two or more circuits are allowed in the same conduit, ducting or trunking system provided the requirements of Section 528 are met". Section 528.1 states that " Every cable or conductor is insulated for the highest voltage present". To comply with requirement one may say that in 230/400V 3-Phase system, each conductor of cables must be rated atleast U0/U=400/692 rather than U0/U=230/400V, and the reason consider we have 3x 1-Phase circuits grouped in same let's say DN50 Conduit, so if one of the conductors(say line  L1)  in the group had insulation failure, the other conductors (of lines L2 and L3) will be exposed to voltage between the conductor and its surrounding medium which is  denoted by U0 of 400V rather than 230V. So here my question is what is the philosophy of section 521.6, which protection it's trying to provide? or shall we use higher rated cables in order to comply? if we must use higher rated cables in case of different circuit, then I think it has some meaning to also mandate using  higher rating in case of conductors of same 3-phase circuit (knowing that  IEC 62440-2008 table 2 allows 300/500V cables to be installed for 230/400V 3-phase system).

Note overall sheath is not taken into consideration as a mean of protection in this section as it is usually doesn't contribute in the voltage rating of cable.

  • if one of the conductors(say line  L1)  in the group had insulation failure, the other conductors (of lines L2 and L3) will be exposed to voltage between the conductor and its surrounding medium which is  denoted by U0 of 400V rather than 230V.

    True, but the same is equally true for a single 3-phase circuit - generally if the insulation is damaged then all bets are off (and let section 434 deal with any consequences). I can't see a physical reason for grouped cables being any different if they're all part of the same 230/400V system.

    I suspect the intend of 521.6 is to deal with mixed voltage systems - e.g. 12V run alongside 230/400V - especially for unsheathed singles in a shared conduit or inside the same multicore cable - in which case you'd want the 12V circuit to have 230/400V insulation, rather than 12V.

    So I reckon that when evaluating "the highest voltage present" you can still treat between-conductors and between-conductor-and-earth separately.

       - Andy.

  • (and let section 434 deal with any consequences)

    The  idea that I suppose there is difference between conductors of same circuit and conductors of different circuit is that section 434 states in its introduction " This section only considers the case of a fault between conductors belonging to the same circuit". So it's a bit confusing here.
     

  • This section only considers the case of a fault between conductors belonging to the same circuit

    Indeed. One of the many "gaps" in BS 7671 (and probably IEC 60364 too). Little protection from small overloads of long duration, the underlying theory of shock protection that's probably not safe for around 5% of the population, 5s disconnection times for larger circuits which is far far in excess of any safe duration for shock protection, nothing to prevent short thin c.p.c.s carrying excess current from faults on larger circuits where exposed-conductive-parts are bridged together by extraneous-conductive-parts. Nothing to prevent end users plugging in large loads in a way to unbalance a ring final circuit and so overload the short leg. The list goes on... Mostly mitigated by the low probability of these things happening in practice and usually tolerable damage, rather than any mathematical or logical certainty.

    Likewise no precautions are demanded for faults between live parts of one circuit and c.p.c.s of another - which would be reasonably plausible in situations like consumer units where conductors of different circuits cross over each other.

    Don't expect any wiring regs to be entirely thorough, complete, consistent or logical.  They might have been once, but have spent over 100 years being quite literally "amended by committee" (or probably more accurately in recent years a hierarchy of several diverse committees), so despite the undoubted best efforts of all those involved, perfection is yet to be achieved.

       - Andy.

  • ,,,, a hierarchy of several diverse committees), so despite the undoubted best efforts of all those involved, perfection is yet to be achieved.

    That is a rather sad but very accurate description of the problem - In many ways regs are  almost an example of something that can either be incomplete or incorrect, but never both correct and complete at the same time as there are always awkward corner cases.

    Mike.

  • well noted thank you  

  •  I agree with you

  • This section only considers the case of a fault between conductors belonging to the same circuit".

    Or, between conductors and Earth.

    This is not so problematic in general ... BS 7671 (and IEC 60364) only considers single fault conditions wherein a fault between two lines requires there to be two breaches of basic insulation.

    The requirements for appropriate mechanical protection (or, 522.8.10, an earthed armour etc.) help to redress this.

    One of the many "gaps" in BS 7671 (and probably IEC 60364 too).

    Given the above, is this really a "gap"?

  • BS 7671 (and IEC 60364) only considers single fault conditions wherein a fault between two lines requires there to be two breaches of basic insulation.

    Indeed, but it could be argued exactly the same for faults between live conductors of the same circuit - yet to omit fault protection would typically be an immediate C2. Maybe faults other then within cables (e.g. at terminations) are more likely to be between conductors of the same circuit - but there are still situations (e.g. CUs and simple DBs) where wires of one circuit run close to terminals of another.

    Plus of course there's the possibility of a single event breaking both layers of insulation together - the old School classic being the floor board nail through a bunch of cables running in the same notch (although I can concede that these days that sort of thing should be mitigated elsewhere - e.g. cable depth/positioning).

       - Andy.

  • BS 7671 (and IEC 60364) only considers single fault conditions wherein a fault between two lines requires there to be two breaches of basic insulation.

    Single damage in an insulation of line conductor(whatever the insulation rating of conductor) will  put the circuit of that conductor in risk of earth fault ,this will not affect neighboring circuits..   

    In a 3-phase system 230/400V if the conductors of all circuits installed in same raceway are rated 450/750V, a single fault of one of the conductors will not affect the other circuits as they can withstand the voltage that is applied on their insulation surface (400V ) because they can withstand 450V. whereas if the cables were rated 300/500V, they will not withstand the 400V applied on the insulation surface.

    The basic question of this thread was query about the philosophy of Section 528.1 (item i and ii ), is it for protecting neighboring circuits from a single insulation fault of a line conductor of a given circuit? if this is was the philosophy, then in 230/400V system, the conductors of different circuits installed in same raceway shall always be specified to be rated atleast 450/750V.

  • The basic question of this thread was query about the philosophy of Section 528.1 (item i and ii ), is it for protecting neighboring circuits from a single insulation fault of a line conductor of a given circuit?

    Like I said, I've seen no evidence (or even any suggestion) elsewhere that there's an intention to protect insulation of one LV conductor after the failure of insulation of a conductor of a different LV circuit.

    528.1 itself is all about mixing Band I (usually ELV) and Band II (usually LV) systems in the same wiring system - so where you only had LV circuits run together, it wouldn't seem to demand any extra precautions at all. (Although other parts of 528 may apply, depending on the circumstances).

    Some others here are closer to the committees' discussions and might be able to enlighten us further - although I suspect that wording goes back quite a time so the original thinking might have been lost in the mists of time by now.