I am sitting on my settee at home with a printed copy of the July/August 2019 Professional Electrician magazine that I picked up off the counter of the WED the electrical wholesaler I use.
In the magazine is This article explaining how under floor electric heating can be installed.
There is this quite clear and unambiguous statement by the NICEIC
Sparkingchip:
SCRDs are not intended to provide isolation.
What if you have a SCRD fused connection unit supplying a 20-amp double pole switch with a flex outlet which the appliance is actually connected to, does that fulfill requirements for isolation?
Andy Betteridge
SRCDs are intended for use in circuits where the fault protection and additional protection are already assured upstream of the SRCD.
RCD Fused Connection Unit for additional protection against electric shocks and fire risk. The unit will remain latched if the power supply is tripped.
ASMTECH:
I installed a dedicated circuit for a hifi system for a customer last year. The customer requested a 6mm2 radial from a 16A MCB housed in its own independent consumer unit into a single, un-switched socket outlet. No problem, bit unusual but no worries.I wired it using a 3c 6mm2 armoured cable as I half anticipated the forthcoming...
The hifi equipment is causing the rcd to trip when started up. I haven't been over to have a look but I am assuming that the startup current for the many power supplies (he has told me there are ten!) coupled with electronic earth leakage is causing a CPC current that is sufficient to trip the RCD (perhaps only 16ma but enough). The earthing is high integrity having a 6mm2 cpc + armour and the Zs is sufficiently low enough that the 16A MCB can be used for fault protection. So, if this wasn't domestic I'd ditch the RCD (or replace with a 100ma) assuming that my assumptions to this point are correct.
The customer has now decided he doesn't want RCD anyway for 'reasons' but I'm still wary of removing it in a domestic situation, not because I believe the installation would become less-safe but just because it contravenes regulations.
Assuming there's no fault on the equipment and it is just a case of startup/inrush current and earth leakage, what approach would you take? Remove the RCD and write it up as a deviation from 7671 with a signed disclaimer/waiver from the customer? Install a 100ma RCD? Do nothing and walk away? Something else?
Sparkingchip:
Okay.
Here is the latest version of the Timeguard BS8277:2016 RCD connection unit
RCD Fused Connection Unit for additional protection against electric shocks and fire risk. The unit will remain latched if the power supply is tripped.
- Provides additional protection against the dangers of electrocution.
- Eliminates the need for plug-in residual current circuit breakers.
- Protects appliances from possible fire hazard.
- Extra fast action – trips out within 40 milliseconds (BS7288).
- Latching for continuous operation after supply interruption.
- Disconnects both Live and Neutral connections leaving Earth connection intact.
I am sure you can see what I am about to point out, that it states twice that the device provides additional protection.
I think it is acceptable to say that anyone other than an electrical engineer that would be additional protection as referred to be BS7671:2018.
Is it additional protection, but not as we know it?