Timeserved:
On my last Inspection which was March 2019 my assessor said it was perfectly fine. I'm with the NIC EIC if it helps.
Regards TS
Chris Pearson:
I am still puzzled by the requirement for one socket.
One socket, one circuit, one CU. All a bit odd, but HiFi buffs have some funny ideas. What really amuses me is that by the time one can afford to spend £tens of thousands, most of us cannot hear the high frequencies which have cost so much. ?
Kelly Marie:
No one yet has said if it really is earth leakage is it not likely to be just the collective high inrush currents of all those PSUs causing a trip and if it is then wouldn't switching to a type D RCBO be the answer. Also if the customer is listening to let's say vinal then why would he need the CD player or Tuner switched on? That really makes no sense. I know of some hi fi buffs who by oxygen free gold plated leads for everything to try to improve the sound waste of money if you ask me. Oh watch out grumpy Kellys out again!
gkenyon:
Timeserved:
On my last Inspection which was March 2019 my assessor said it was perfectly fine. I'm with the NIC EIC if it helps.
Regards TS
Not sure what the rationale is, to be honest. BS 7671 clearly lists the standards for RCDs recognised for providing Additional Protection. If you haven't used an RCD complying with one of those standards, that's a departure (but may be no less safe, therefore OK, but still need to state the departure).
Of course, whatever the situation, additional protection by 30 mA RCD may be required for other reasons, e.g. cables concealed in walls < 50 mm from the surface.
Hi Graham,
Sorry forgot to mention that the cables were surface ran in galv conduit, so in this instance the additional protection was only for the user and not required for the fixed electrical installation.
Regards TS
Therefore, I'm still unsure as to the rationale for the assessor stating it was OK
The residual current device at socket-outlet level is normally intended to be installed by skilled or instructed persons. It can be operated several times per day. The isolation function is not necessary since pulling out the plug from the socket-outlet is recognized as providing effective isolation.
SRCDs are neither intended to provide an isolation function nor intended to be used in IT systems.
SRCDs are intended for use in circuits where the fault protection and additional protection are already assured upstream of the SRCD.