I have a situation here designing an 200kW EV charger.  The manufacture of the charger supplies a gland plate with 10no entry glands for single cores in parallel.  The distance between the gland plate and the busbars of the charger is quite small meaning glanding and terminating a multi-core cable would make it very difficult to navigate the cores to the busbars.  The charger itself does not require a neutral.  

In appendix 4 in the brown book, there is no reference D for single core armoured cables, just Ref C and F.   When looking further back in the book on p431 is does say that if the specific installation parameters are known (ground thermal resistance, ground ambient temp, cable depth) you can reference the cable manufacture or ERA69-30 series.    I have a copy of ERA which has the current carrying capacity tables for three single core armoured underground but my main question is this:-

Does that paragraph for Ref method D only apply to multicore cables in the ground, and therefore single core AWA buried is not compliant with BS7671 and cannot be certified? 

Thanks in advance  

Parents
  • Dan20387,

    I think I know the charger you are talking about? Think manufacturers name is Al..... and an Italian manufacturer.

    What I have done is get them to supply a gland plate with no entries punched in it. Charger was then installed in two x four core H0FR7 cables in parallel.

    Myself and my clients rejected their standard gland plate and if they wanted our business then supply what we requested.

    Other thing is they supply a connection "Jig" so base plate is bolted onto foundation after you glanded your cables in then you fit the jig. You have tons of space as the main charger enclosure isnt yet bolted on, so you dress/bend/form the conductors. Fit crimps and bolt them to the studs on the jig. That way your conductors are all sorted for install.

    You then unbolt the conductors remove the jig and then the main charging enclosure is lifted on. And because your conductors already shaped and lugged, then easy to then bolt on your conductors. Job Done.

    But, avoid the single armours at all costs.

    Cheers GTB

Reply
  • Dan20387,

    I think I know the charger you are talking about? Think manufacturers name is Al..... and an Italian manufacturer.

    What I have done is get them to supply a gland plate with no entries punched in it. Charger was then installed in two x four core H0FR7 cables in parallel.

    Myself and my clients rejected their standard gland plate and if they wanted our business then supply what we requested.

    Other thing is they supply a connection "Jig" so base plate is bolted onto foundation after you glanded your cables in then you fit the jig. You have tons of space as the main charger enclosure isnt yet bolted on, so you dress/bend/form the conductors. Fit crimps and bolt them to the studs on the jig. That way your conductors are all sorted for install.

    You then unbolt the conductors remove the jig and then the main charging enclosure is lifted on. And because your conductors already shaped and lugged, then easy to then bolt on your conductors. Job Done.

    But, avoid the single armours at all costs.