broadgage:
I would be inclined to remove the trunking lid VERY gently and whilst wearing leather gloves, a full face visor, and a flame resistant overall coat. AFTER explaining to the customer what might go wrong, and that you are not replacing it all FOC if it all goes orribly wrong.
Yes, that may be necessary. My customer is only a tenant. He seems reluctant to speak to the owner of the installation. Just a feeling I have.
Z.
Zoomup:
Just a feeling I have.
"Go with your guts" was an aphorism which I learned many years ago. Your gut feeling is, in fact, a sub-conscious analysis of the situation. Zoomy, you are clearly experienced enough to have plenty of guts. ?
When I did my training, we were given the acronym "SILT" for safe isolation - switch off, isolate, lock off, test. I reckon that it should be "PSILT" with a silent P as is psychiatrist. The P stands for "permission".
Removing trunking lids sounds as dodgy as removing the wings off a TR2. If the bolt head shifts at all, it simply shears off. Then where do you stand?
Afraid that I must still advise trial and error.
ETA: put yer tin 'at on. Isolate one by one and see who comes at you with a loaded 12-bore. ?
mapj1:
-----
If you are brave you could try injecting a modest current onto the armour - ideally you'd need to lift the earth at the load end and that may not be possible or safe.
However, assuming the armour is the CPC, or at least part of the CPC, then pulling an L-E fault current of a few amps ought to allow the correct SWA to be isolated with nothing more than a clamp meter over the jacket of each SWA in turn to identify the one that reads more when the 'fault' current flows. Please check Zs first of course.
Caveat, I may not have the right mental picture of the installation .
It is of course silly to ask why are they not labelled, and what the official emergency isolation process is.
Mike.
Not certain that this will work. A clamp meter applied around the outer jacket of a SWA should read about zero. If the current flows "out" along the phase conductor, and "back" via either the neutral conductor or via the SWA, the NET current is still zero, excluding any minor leakages from other circuits.