broadgage:
Even if not actually prohibited I would consider it poor practice to have 24 volts DC fully exposed to touch in a wet location such as bathroom.
I would consider that 24 volts DC should be at least somewhat enclosed or protected against touch, though not to the same standards expected for mains equipment.
A non shuttered socket outlet for 24 volts DC, fine.
A within reach lamp holder for 24 volts DC fine.
A "tension wire" lighting system at 24 volts DC not good practice. Nor a similar voltage on exposed door hinges.
I perceive some risk of poor contact, and the user fiddling with it with wet hands.
The comparison with lights on lorries is relevant, only one pole of the supply is EASY to touch being connected to the body of the vehicle. The other ole of the supply is much less easy to touch being present on recessed lamp holder contacts and the like.
It is prohibited, BUT only in Zones 0, 1 and 2, see Regulation 701.414.4.5 of BS 7671
701.414.4.5 Requirements for SELV and PELV circuits
Where SELV or PELV is used, whatever the nominal voltage, basic protection for equipment in zones 0, 1 and 2 shall be provided by:
(i) basic insulation complying with Regulation 416.1, or
(ii) barriers or enclosures complying with Regulation 416.2.
If the bathroom cabinet is not in Zone 1 or Zone 2 (effectively more than 0.6 m away from the bath or shower) then there is no requirement for basic protection.
gkenyon:broadgage:
Even if not actually prohibited I would consider it poor practice to have 24 volts DC fully exposed to touch in a wet location such as bathroom.
I would consider that 24 volts DC should be at least somewhat enclosed or protected against touch, though not to the same standards expected for mains equipment.
A non shuttered socket outlet for 24 volts DC, fine.
A within reach lamp holder for 24 volts DC fine.
A "tension wire" lighting system at 24 volts DC not good practice. Nor a similar voltage on exposed door hinges.
I perceive some risk of poor contact, and the user fiddling with it with wet hands.
The comparison with lights on lorries is relevant, only one pole of the supply is EASY to touch being connected to the body of the vehicle. The other ole of the supply is much less easy to touch being present on recessed lamp holder contacts and the like.It is prohibited, BUT only in Zones 0, 1 and 2, see Regulation 701.414.4.5 of BS 7671
701.414.4.5 Requirements for SELV and PELV circuits
Where SELV or PELV is used, whatever the nominal voltage, basic protection for equipment in zones 0, 1 and 2 shall be provided by:
(i) basic insulation complying with Regulation 416.1, or
(ii) barriers or enclosures complying with Regulation 416.2.
If the bathroom cabinet is not in Zone 1 or Zone 2 (effectively more than 0.6 m away from the bath or shower) then there is no requirement for basic protection.
Thank you all for taking your time to read my post and provide comments; it's appreciated.
Graham, your quote above is enough for me to go on. I checked with my copy of BS7671:2018, and I'm pleased to read 701.414.4.5 (for others reference, page 241), as the cabinet is intended to be installed in Zone 1, according to the customer. Considering the mirror cabinet will be installed in a bathroom, I feel I can negate the need for other standards and quote section 701. Any electrician who comes to install the mirror should be checking BS7671; hopefully, they'd see 701.414.4.5, leading to a refusal to install the cabinet in a bathroom. Thank you, Graham; I should have looked at section 701 before asking this question!
Kind Regards, Harry