AJJewsbury:switched via PID for temperature control
How does the PID (proportional–integral–derivative) temperature controller vary the power? If it's chopping the a.c. waveform (like a big dimmer) as I understand some do - I'd be very wary of putting RCDs downstream of it.
Andy, I think that you meant upstream.
Chris Pearson:AJJewsbury:switched via PID for temperature control
How does the PID (proportional–integral–derivative) temperature controller vary the power? If it's chopping the a.c. waveform (like a big dimmer) as I understand some do - I'd be very wary of putting RCDs downstream of it.Andy, I think that you meant upstream.
This time I did mean what I wrote ? - there have been suggestions for individal RCDs (RCCBs or RCBOs) for each immersion heater - which would have to go downstream of the controller. I really don't like the idea of feeding an RCD a non-sinusoidal supply (the potential for the residual current being non-sinusoidal is another issue).
- Andy.
AJJewsbury:Chris Pearson:AJJewsbury:switched via PID for temperature control
How does the PID (proportional–integral–derivative) temperature controller vary the power? If it's chopping the a.c. waveform (like a big dimmer) as I understand some do - I'd be very wary of putting RCDs downstream of it.Andy, I think that you meant upstream.
This time I did mean what I wrote ? - there have been suggestions for individal RCDs (RCCBs or RCBOs) for each immersion heater - which would have to go downstream of the controller. I really don't like the idea of feeding an RCD a non-sinusoidal supply (the potential for the residual current being non-sinusoidal is another issue).
I thought that we had reached the conclusion that we just need an RCBO in the DB if at all. However, I interpreted your message as being cautious about the type of RCBO. i.e type AC might not be compatible with the PID, but type A might. AFAIK, TPN RCBOs are type A.
I thought that we had reached the conclusion that we just need an RCBO in the DB if at all.
However, I interpreted your message as being cautious about the type of RCBO. i.e type AC might not be compatible with the PID, but type A might. AFAIK, TPN RCBOs are type A.
AJJewsbury:
We've got I think a total of 27kW - so at least 40A/phase - as I've not seen any 3-phase RCBOs rated that high yet (usually 32A max) I suspected that an upstream RCBO might not have been intended.
So can we agree that RCD protection is not required? I must say that I don't see any requirement for it as far as this circuit is concerned.
Higher current ones do exist that would do, (63 amp example) but not in great numbers or variety or indeed from the famous names.
An RCD incomer and followed by MCB protection might be easier to source the bits for.
So can we agree that RCD protection is not required?