wallywombat:
They seem to have converted the existing confusing criteria into a new set of completely bewildering criteria. If I am reading the draft 443.4.1 correctly, it summarises as:
- Must protect if could result in risk of injury/life or financial / data loss.
- Except single dwellings, if intolerable (as decided by all parties), do risk assessment to decide if protection required.
- Protection not required for single dwellings with not much to lose (except it notes that most will have much to lose).
So they don't actually state what you should do for single dwellings with valuable electronics. It certainly doesn't state that you need SPDs, nor that you need to a risk assessment.
That is pretty much exactly as I see it.
gkenyon:Chris Pearson:
So do we do risk assessments for single dwelling units or not?"Except for single dwelling units ..."
(I have raised a comment on the apparent typo.)
"Stroke" is 100 % correct, and aligns with BS EN 62305-series.
Graham, thank you. Every day is a learning day in this forum. ?
IMHO the proposed 443.4.1 would be clearer if the exception for single dwelling units were removed. As it stands, if the risks are considered to be tolerable, no further action is required. Note 4 refers to determining the total value of loss in dwellings and then it is up to the occupier to compare the cost of SPD with the possible loss, i.e. to make a judgement as to whether the risks are tolerable. What does not seem logical is to exclude dwellings from the risk assessment because it may show that SPD is not justified. (Of course there is nothing to stop an occupier or his electrician doing a risk assessment in any case.)
I also think that the difference between suburban and urban should be clarified though I struggle to determine where the boundary lies within this borough.
I would also add that the more I think about it, the more I feel inclined to install SPD at home.
Chris Pearson:Graham, thank you. Every day is a learning day in this forum. ?
IMHO the proposed 443.4.1 would be clearer if the exception for single dwelling units were removed. As it stands, if the risks are considered to be tolerable, no further action is required. Note 4 refers to determining the total value of loss in dwellings and then it is up to the occupier to compare the cost of SPD with the possible loss, i.e. to make a judgement as to whether the risks are tolerable. What does not seem logical is to exclude dwellings from the risk assessment because it may show that SPD is not justified. (Of course there is nothing to stop an occupier or his electrician doing a risk assessment in any case.)
I also think that the difference between suburban and urban should be clarified though I struggle to determine where the boundary lies within this borough.
I would also add that the more I think about it, the more I feel inclined to install SPD at home.
I can't disagree with you here Chris. I think the real turning point will come when insurers don't pay out for an event simply because SPDs weren't fitted.
Don't forget, though, telephone master sockets may not have SPDs in them any more - so if you've got wired network devices and haven't got FTTP, you might want to surge protect your phone/broadband line too.
I'd prefer something like a number from 0..10 based on the roughly estimated percentage of open space in the 1km square surrounding the property (parks, fields etc) - assuming of course that that's what the urban/suburban/rural disctinction is supposed to be about.