How about an RCD assembly incorporating a switchable parallel feed (by a special key?) which could be put in circuit whilst the RCD is tested? Straight away I can see that for the duration of the test the circuit may not conform to regs, but maybe with a Risk Assessment and suitable control measures in place this could be overcome. Just an idea.....
two RCDs with a make before break switching arrangement wont work and you would drop your load. parallel paths would imbalance the currents through the rcds which would operate and drop your load.
AJJewsbury:
two RCDs with a make before break switching arrangement wont work and you would drop your load. parallel paths would imbalance the currents through the rcds which would operate and drop your load.Ah yes, good point. Same problem with a single RCD and a by-pass switch then too. Back to the drawing board....
- Andy.
Foffer:
AJJewsbury:
two RCDs with a make before break switching arrangement wont work and you would drop your load. parallel paths would imbalance the currents through the rcds which would operate and drop your load.Ah yes, good point. Same problem with a single RCD and a by-pass switch then too. Back to the drawing board....
- Andy.
How about a purpose made assembly using two RCD's with tripping mechanisms that are disabled during switching, an interlock to make sure that both were not left on together and a system for provision of testing the one out of circuit. It's getting a bit complicated now!
Ruggedscot:
again zero point only valid for resistive loads, but with modern switchmode and inductive capacitative loadings that zero point would be hard and the switching timeframe tiny. sometimes we chase a solution and become blinded by the desire to identify that solution, when the reality is that it could be done simpler and easier through planning the work and having buy in from others. there is no process that can not be interrupted for a short time if all the required planning and adjustments are in place.
lyledunn:
Interestingly the National Rules for Electrical Installations in Ireland (ET 101:2008) permit omission of RCD protection for socket outlets for IT equipment and socket outlets used for isolation of fixed equipment. Caveats apply. Not sure if this will alter in the new edition scheduled for publication in January 2020.