Alan Capon:
You would need sight of the Fire Risk Assessment to determine if they are suitable. You also need to know what the fault is on the Gent panel and what it’s affect is. If for example, the fault prevented some of the self-closing fire doors from operating, then replacing the failed detector(s) with a system that can not close the doors would seem to be inappropriate. If the new detectors alert the managing agents, but they cannot remotely close the fire doors, this would also seem inappropriate. The BS spec for fire alarms requires a percentage of detectors to be held as stock, so assuming a competent fire alarm company is carrying out the work, the provision of spares can not be an issue.
Regards,
Sparkingchip:
Guide to BS 5839-1 by Colin S. Todd