Simon Barker:
Because one switch on its own isn't "switchgear", whether or not it's "similar" to a CU. Put two of them together in the same box, and that's another matter.
AJJewsbury:
I think that a double pole switch does meet the definition of switchgear as defined in Part 2
I hope you're wrong - otherwise we'll start to need metal clad rotary isolators and FCUs. Where's the "auxiliary" switching equipment when you only have a single switch disconnector in a box?
but think about what the regulation is intended to do
Distract attention away from CU manufacturers making plastic cases that weren't quite as self-exitinguishing as the standards required?
- Andy.
I'm sure there are metal enclosure versions of "REC" switches out there.
At the end of the day, the argument about the DNO device not protecting the "tails" is what it is ... I'd guess their stance is also a result of the "consumer unit fires" issue also. Basically, in every case where the metal-cased REC isolator is not considered suitable, neither is a metal-clad consumer unit that doesn't provide double insulation or equivalent for the busbars (and upstream devices) feeding the protective devices that provide shock protection.
531.3.5.3.2.201
For Class I enclosures in TT systems where RCD protection is used on outgoing circuits, double or reinforced insulation of all live conductors (incoming cables, extension terminals, etc.) on the supply side of the incoming device, e.g. main switch, shall be used. Insulated and non-metallic sheathed cables are deemed to meet the requirements of double or reinforced insulation.
NOTE: Consideration should be given to the manufacturer's internal live interconnecting cable links on the supply side of an RCD being double insulated, having reinforced insulation or equivalent mechanical protection.
mapj1:
531.3.5.3.2.201
For Class I enclosures in TT systems where RCD protection is used on outgoing circuits, double or reinforced insulation of all live conductors (incoming cables, extension terminals, etc.) on the supply side of the incoming device, e.g. main switch, shall be used. Insulated and non-metallic sheathed cables are deemed to meet the requirements of double or reinforced insulation.
NOTE: Consideration should be given to the manufacturer's internal live interconnecting cable links on the supply side of an RCD being double insulated, having reinforced insulation or equivalent mechanical protection.
To me the 'NOTE' is not strong enough. You may consider it if you like but it rather leaves the door open to misinterpretation . To have insulated and sheathed meter tails into to a DIN rail main switch, but then some bare bus bar to take live feed from the switch to a row of RCBOs, or in the CU of at least one well known brand what looks like very thick enameled wire to the RCDs appears to be acceptable, so in one case nothing and in the other only varnish insulating a pre RCD live, and I rather think it should not be.
I'd be far happier if it said "double or reinforced insulation is required for all wiring not protected by an RCD or RCBO"
It does not.