But this is precisely why I asked the specific question whether you were advocating 30 mA RCD protection for couplers as well!
In fact, I agree it's a difficult situation to grasp, but at the end of the day the Reg exists for "couplers" separate to "socket-outlets", and I can't see the difference between "appliance outlet" and "free outlet" in the context of a cable coupler.
So, the question - should couplers be included in 411.3.3 ? I sort of think you're saying they should be.
IT cabinets are 3 Phase and I dread the thought of an IT Technician interconnecting the power to dual fed Servers for obvious reasons.
It would seem more that a little absurd that where a 32A BS EN 60309 wall mounted socket needs 30mA RCD protection, a wall mounted isolator with a stuffing gland supplying 6" of flex with a 32A BS EN 60309 female coupler on the end of it, in the same situation, would be exempted. (I note that the title of BS EN 60309 is "Plugs, socket-outlets and couplers..." so that's no help.)