Alasdair Anderson:
This is to do with circuits for Safety Services, defined as:
Safety service. An electrical system for electrical equipment provided to protect or warn persons in the event of a hazard, or essential to their evacuation from a location.
Based on this I would not classify dedicated medical IT final circuit cabling as a safety service and so this requirement would not apply.
Others may have different opinions of course.
Alasdair
Roy Bowdler:
I recall a situation some years ago in which Bed Head Trunking produced by a particular supplier had been specified by the designer, on the basis that it had been “approved as a medical device”. Our design department pointed out that other supplier’s containment was substantially the same, but available at much lower cost. I can’t recall the overall cost difference, but it would have been 100K plus. So we have an ambiguous situation involving several powerful stakeholders, with one or more potentially standing to lose money.
Graham makes the point well and illustrates that engineering judgments are often about coming to an optimum solution (aka compromise) not theoretical “perfection”. I also don’t recall the outcome, although readers familiar with current policy around HTM 08-03 may be more familiar.
I think in reality this this needs addressing in the next version of the HTM otherwise Contractors will continue to be scared of non-complying to the regulations unless they use fire rated cabling.
.....Any proposed departures, including any equivalent or mitigating measures to be applied, should be discussed with the relevant stakeholders
including the Electrical Safety Group....