Hi everyone, I am looking for some answers for the following situation:
There are two identical three phase step-down transformers 11kV to 0.4kV, connected to a 11kV ring main, each have an UPS system connected downstream and both are connected to the same Automatic Transfer Switch:
TX1 → UPS1 → ATS SOURCE 1
TX2 → UPS2 → ATS SOURCE 2
I want to plug in a parallel supply ciruit in the ATS for source 1 (considering the new and existing circuit would be live) and I want to double check by measurement that the new circuit is not connected to another source by mistake.
I have measured at the ATS the voltage and frequency on the same source, U=400V / Uo=230V / 50Hz and I wasn't expecting any voltage between the two separate sources but this is what i found:
TX1/ L1 - TX2/ L1 = 2V / 700-800Hz
TX1/ L1 - TX2/ L2 = 400V / 50Hz
TX1/ L1 - TX2/ L3 = 400V / 50Hz
TX1/ L2 - TX2/ L1 = 400V / 50Hz
TX1/ L2 - TX2/ L2 = 2V / 700-800Hz
TX1/ L2 - TX2/ L3 = 400V / 50Hz
TX1/ L3 - TX2/ L1 = 400V / 50Hz
TX1/ L3 - TX2/ L2 = 400V / 50Hz
TX1/ L3 - TX2/ L3 = 2V / 700-800Hz
From the readings above I can see that the different frequency between TX1/ L1 and TX2/ L1 etc is an indicator of a different source of supply.
Is my assumption correct?
Why is there a voltage between the two sources of supply if there is no physical connection due to the internal windings in the transformer?
Why is there a highly fluctuating frequency between the same lines of the two sources?
Thank you in advance!