Simon Barker:
The intention is that you can isolate the whole installation with one switch, rather than having to flip a whole bank of breakers. If there is a main switch in the distribution board, then that is the isolator. Otherwise, there should be an isolator before the DB.
If it's a DB, then that implies that it's just one part of a larger installation. In which case, is there an isolator at the origin of the supply?
Graham Kenyon:
Don't forget, in accordance with BS 7671, isolators for LV systems must disconnect ALL poles (including Neutral), unless the supply is a TN system (TN-S or TN-C-S) in which isolation of the Neutral is not always required.