A 4 mm² spur might not fit if taken off at a socket (2 x 2.5) + 4 > 8.
AJJewsbury:A 4 mm² spur might not fit if taken off at a socket (2 x 2.5) + 4 > 8.
Nothing says you have to take all the conductors directly into the socket terminals - if they won't fit you can always (US style) take a selection into a floating terminal in the back-box and then have just a fly-lead to the socket itself.
Yuk!
Or just use a better quality socket with 12 mm² terminals, but Sir prefers Screwfix's cheapest.
Simon Barker:
If his thinking is that he is going to have a desk for working at, then trying to plug a PC and monitor into 2A or 5A sockets is going to be a right pain.
What's wrong with a 13A FCU at the origin of the spur, and as many 13A sockets as is needed at the floor box?
That would do the job, but is perhaps a little restrictive if say a space heater, a kettle and a laser printer are to be used.
ebee:
Well I`d question does he really really need a floor socket.
That's not for us to say, but to my mind, it is very odd. It is a newly retired couple's house. Downstairs, there will be a kitchen with ample room for day-to-day eating; a dining room; and the drawing room. I dare say that the latter two will only be used when they have company, say Christmas and Easter. If you withdraw after dinner, you'd be supping brandy and making polite conversation. (Though to be really authentic, the ladies would withdraw, and God knows what sort of conversation they would have.)
He wants them for things like table lamps and a wireless, but why would you be reading or listening to the wireless, or both in the drawing room? He can do that in the "library" upstairs. (That's having floor sockets as well.) ?
Simon Barker:
If his thinking is that he is going to have a desk for working at, then trying to plug a PC and monitor into 2A or 5A sockets is going to be a right pain.
What's wrong with a 13A FCU at the origin of the spur, and as many 13A sockets as is needed at the floor box?
Desk, assuming that there will be one, will be in the library. I quite agree - an FCU at the origin of a spur is a good idea. Clutters up the wall though!
Some of the kitchen sockets will be in the window recesses (think stone cottage or a castle). You try working out the safe zones for that! ?