Chris Pearson:
Link
If you look carefully, the second I is wearing a little hat, thus: Î. It is not defined in the text nor in section 2 of BS 7671.
Well yes Chris, you are right, I had to use a magnifying glass to see that. I thought that it was just ( and ). So, what does the hat mean?
Z.
gkenyon:
In this case, (I2t) is the let-through energy of the device quoted by the manufacturer, or obtained from BS EN 60898 or BS EN 61009, and I2 in the denominator (divisor) is the square of the prospective fault current.
Example
For a B32, the BS EN 60898 maximum let-through energy (I2t) is 45,000 A2s. The lowest prospective fault current in the circuit is (measured or calculated to be) 1000 A.
Therefore, I2=1,000,000, and t ≈ 45,000/1,000,000, so t ≈ 0.045 s.
Usually, the manufacturer's quoted let-through energy (I2t) is much lower than BS EN 60898, and so the approximate tripping time will be less than the value calculated from the BS EN 60898 data.
Thanks G.K. I am trying to get my head around energy let through. I am partially there. The numbers are difficult to visualize as they are either so BIG or so small. Or the figures have no units.
Z.
I was wondering what the horizontal "I/In" meant. "In" would make sense. I presume that it means I or In, rather than I divided by In.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site