mapj1:
Having said that, where liquids and electrics meet RCDs are a very nice thing to have, even if the RCD covers more than one immersion heater.
(https://www.tlc-direct.co.uk/Products/WYWRS32slash4.html) sort of sized object.
Cheers. I was hoping to keep all elements on separate circuits, so if one develops a fault the other 3 will continue to operate, and any fault will be easier to detect. At present the Control Panel has 6 individual circuits, with Rail Mounted Cartridge Fuses and Contactors installed on each. I understand that the Control Panel can be fed either via a Henley Block or from the 3-Phase Distribution Board? Wondering if an enclosure with RCD would be an option?... https://www.cef.co.uk/catalogue/products/1051602-3-module-insulated-ip65-enclosure
davezawadi (David Stone):
I do not expect you to be heating things if no operator is present, so a single RCD covering everything would be perfectly satisfactory. I suggest the plugs and sockets are a good idea in any food area, as cleaning is much easier if things are all on castors. That and a 3ph board are not too expensive and save the isolator cost completely, you simply unplug items to isolate. You may find 3 circuits, of 16A each perfectly satisfactory for the moment, with 16A BS4343 sockets (red) but leave space in the board for expansion later! IP67 ones are probably unnecessary unless you live in a permanent spray of water, which I doubt! Turn off the RCD before using a pressure washer.
Cheers David. It does sound like the general consensus is to use an RCD. Wondering if I'm worrying too much about things developing faults? Maybe I should go with a single RCD feed from the 3-Phase Board to the Control Panel. At present the Control Panel has 6 individual circuits, with Rail Mounted Cartridge Fuses and Contactors installed on each. I do also need to be able to switch the individual elements (9kW, 9kW, 6kW, 3kW) on/off to control or ramp up temperatures.
Chris Pearson:
Could you not have an RCD incomer in the DB?
Cheers Chris. I was hoping to keep all elements on separate circuits, and also have RCDs on all circuits, just so if one develops a fault the other 3 will continue to operate, and any fault will be quicker and easier to detect?
Nano Brewery:Chris Pearson:
Could you not have an RCD incomer in the DB?Cheers Chris. I was hoping to keep all elements on separate circuits, and also have RCDs on all circuits, just so if one develops a fault the other 3 will continue to operate, and any fault will be quicker and easier to detect?
No, I wouldn't look at it that way. Each element will have its own MCB/fuse. A short circuit would trip the MCB, but not the RCD. A fault (i.e. to earth) might trip both. Ok, that is a bit of a bother if the whole lot goes off. I am not sure how that affects your business, but if it slows down a batch, is that an issue? If it occurred, you can still isolate the faulty element by its MCB.