mapj1:
its not new - its how the green rot spreads along wiring in cars. However, only short lengths breathe significantly, and solid core cables not at all. If you really cannot manage it, then gel filled cable is the answer
perspicacious:
I don't consider the "symptoms" described here are capillary in a strict definition. It is more of a pumping action.
Regards
BOD
perspicacious:
I don't consider the "symptoms" described here are capillary in a strict definition. It is more of a pumping action.
Regards
BOD
Now consider an IP rated enclosure, is it better sealed or with a drain hole in the bottom of it?
Sparkingchip:
A drain hole will equalise the pressure inside and outside of the enclosure, so moisture won’t be “pumped” through the cables.