AJJewsbury:
. . . When comissioning on site however I would have thought it would be difficult simulate many of those conditions (you obviously can't mess with the real grid so you'd almost need your own little power plant with controllable frequency to simulate nasty grid conditions) . . .
Jam:
. . . I'm reviewing the Loss of Mains protection for a number of old (pre-2018) G59 type tested inverters. . .
. . . Does anyone know where it states which method is used?. . .
When comissioning on site however I would have thought it would be difficult simulate many of those conditions (you obviously can't mess with the real grid so you'd almost need your own little power plant with controllable frequency to simulate nasty grid conditions) - so would have imagined that the test would be just to open a handy disconnector between the inverter and the grid and time how long it takes the inverter to notice and disconnect - in effect simulating an extreme case for all the monitored variables all at the same time. So in a way the on-site test produces a time, but it can't be related to any particular detection method.
Indeed, and this is the reason behind the certificated “type tested” inverters, whether they are certified to G.59, G.83, or the newer G.98 or G.99 standards. If however you modify one or more of the inverter parameters, the type-test certificate becomes invalid and my understanding is that the inverter can no longer be legally connected to the public supply without re-certification.
It will be stated on the type-test certificate, either directly, or due to the values quoted.
Where the requisite RoCoF setting cannot be achieved without additional investment, remove LoM protection from all generation except for synchronous and doubly-fed induction (DFIG) units