Question
hi people, I’m new to the forum, and seeking a bit of advice. My shed (well it’s more of a small open fronted barn/fire pit area) is about 20 metres from the house. Requirement is to run a couple of sockets (or two pairs) and a couple of lights.
I have a length of 3core SWA cable and some existing outdoor sockets on the side of the house.
my thinking is to put the SWA straight in to the existing double socket, run it down the garden (digging in) and in to a junction box to supply the sockets.  The lighting could also be plugged in to the sockets if it made it simpler.
only likely to be running the odd power tool, radio, lamps or other such stuff, fairly light use.
Does this sound ok?
8 Replies
mapj1 80733779
Joined 22/07/2004 - 1910 Posts
Good. You pretty much always should connect  the armour to the earth at the supply end, for all the common house earthing arrangements.
However the earth at the load end may or may not be taken from the armour, it may instead be that the armour is insulated, and earth taken from a local electrode, depending if it is better to create a TT island for the load - examples where it is better to have a local earth rod and not use the suppliers earth at  the load end, when the suppliers earth is PME /TNC-s include for car charging points, swimming pools, areas with earth floors and livestock, caravan pitches, and a few other situations. Examples where you would use the house earth are if it has a dry wooden floor and all the electrical items are domestic, and essentially indoors.
Between those extremes lies a large  area requiring some thought.
Stillfirm 11001213437
Joined 19/11/2019 - 2 Posts
Thanks guys, back to the more info required qs - I’ll come back with some more info. I fitted SWA previously for some outdoor sockets onto appropriate junction provided by my electrical contractor - and earthed it 😀👍
Zoomup 1100345625
Joined 23/10/2014 - 1751 Posts
Exactly, you (experienced electrical engineer person) know what to look for in the electrical dept. whilst playing with the spiders under the floor boards. 

Z.
Chris Pearson 11001208764
Joined 05/12/2018 - 1367 Posts
Judging by the horrors under my daughter's floorboards electricians should not dabble in the sacred art of electrical engineering. 😯

The interesting thing is that virtually all, if not all, of the defects have been revealed on inspection rather than testing.
Zoomup 1100345625
Joined 23/10/2014 - 1751 Posts
Yes, that is exactly it Chris. That is why unqualified people should not dabble in the sacred art of electrical engineering. They should leave it to us, the professionals, don't you think?

Z.
Chris Pearson 11001208764
Joined 05/12/2018 - 1367 Posts

Zoomup:
The cable did not have the armour earthed, well it was not even connected.

I must say that it is not at all obvious to a lay person that the armour should be earthed; it seems reasonable for a lay person to assume that the purpose of the armour, as with other forms of armour, is to provide mechanical protection.
Zoomup 1100345625
Joined 23/10/2014 - 1751 Posts
I have just undertaken a consumer unit renewal. The house was previously owned by a builder. The new owners are having lots of work done including a new kitchen. The builder had run an S.W.A. cable from the back of a downstairs' room socket through the wall to a pond pump position. The cable did not have the armour earthed, well it was not even connected. The outdoor socket was an ordinary indoor type on a pattress mounted on a low wooden stake. No R.C.D. protection at all. The circuit was protected by a B.S. 3036 30 Amp fuse.  The socket was protected from the elements by a removable wooded "hat" that wobbled a bit on the socket stake. Needless to say I disconnected the cable.

Z.
mapj1 80733779
Joined 22/07/2004 - 1910 Posts
More info needed. 
1) how are the existing sockets supplied - own circuit, or spurred off the house ring, or just hung off the back of the light switch  ? You need to know, and to be sure they are in fact supplied correctly to begin with, i.e. from a circuit that can take the load, and the supply cable is co-ordinated with the rating of the fuse or breaker, and there is RCD protection.
If they are spurred off an existing ring, it is a very good idea  to add a fused spur or RCD spur with a switch inside the house to protect just the outdoor bit, than you can isolate it when you go on hols or if water gets in.

2) This SWA - what is it's copper cross section? - for sockets over that distance I'd expect at least 2.5mmsq if the circuit fuse or breaker was 20A or less. Perhaps 4mmsq. Again, the cable size needs to co-ordinate for the rating of rest of the circuit. Look up how to terminate the IP rated glands unless you already know what you are doing.
3)Digging in  - if it is not under a concrete path, I'd suggest aim for half meter down or more, in case the garden gets dug at some point.

4) Earthing. How is your house earth, TT, TNS or TNC-s . Also is the shed floor timber and dry, or cement or earth or possibly damp, and is it possible you may plug something in and take it outside ?
Please confirm all these things, as it affects what is recommended for the earthing at the shed end of thing

5) Using a fused spur off the power cct.  for the light switch at the shed end may be OK - but you do need to think about what happens if lights all trip off due to a faulty appliance  - emergency lights or any critical loads.

So in summary it may well be OK, but it depends.





 