I have as an incomer parallel 95mm2 singles AWA armoured.
That is 2-off L1 cables, 2-off L2 cables, 2-off L3 cables, 2-off N cables and an earth
All together 8 cables excluding the earth.
We are using method of installation "BICC data - In underground single way ducts"
What does this mean to you?
As I interpret it, we need 8-off ducts one per cable.
Am I right???
If I use the L1s in one duct, the L2s in another duct, the L3s in another duct and the Ns plus E in another duct is it acceptable? Or it is a violation of the installation method and the cable ratings are not valid any more?
Also another question.
In the grouping factor section it asks me about "spacing"
If we have one duct per cable, the spacing is about the ducts between them. Isn't it?