AJJewsbury:
I guess the "correct" answer (according to standards) is a BS EN 60309 2 pole + PE connector with the earth at the 3h position (in white) - which is specifically for 50-250V d.c. Where you'd source such as beast from I've no idea though (I don't recall ever seeing such a thing even in a catalogue never mind real life).
davidwalker2:
An alternative I have had suggested is to use a 16A 3-pole Schuko plug and socket. It is a controlled, industrial situation, and we do not have any equipment on site that uses continental-style connectors, they are readily available and cheap. Any thoughts?
David
davidwalker2:
Again, many thanks for your replies. The Guide recommended by Graham is very useful and addresses many things we have needed to resolve over the years. Unfortunately it rather cops out on the connector issue, stating that “the standards required by this legislation [Plugs and Sockets (Safety) Regulations] restrict the use of general-purpose socket-outlet circuits for currents of 13 A or less operating at LV d.c. in relevant parts of electrical installations.”
For information, on our site the main dc source is a 200A mercury arc rectifier (see my avatar) backed by a lower power solid state supply (40A). Fuses are BS88 dc types, disconnectors are heritage (1928) open frame, and a couple of modern dc contactors. Our major problem has been wire colours, red/black on the oldest heritage cabling, brown/blue on later heritage modifications. We have chosen not to introduce a third combination, the current standard brown/grey and rely on separation, clear labelling and a competent expert workforce.
David