Current in HVDC power transmission

Former Community Member
Former Community Member
Does anybody know the current over electric cable in HVDC is relative constant current or other uncertain wave(like the wave after single phase bridge rectifying)?

Is there any enforcing standard or industrial standard? Thanks~
  • The standard is usually set in accordance to the customers specification. However, transients resulting from changes in the current order are well damped by responding with an overshoot less than 5% and with a maximum settling time of 200ms.