Bonding of a bolted-together equipment rack located in a vehicle

I have a custom built stainless steel equipment rack that is made up of many individual sections of stainless steel angle that are bolted together to form the complete rack. The stainless steel parts will not have any paint or finish applied. 

The equipment rack will be mounted in a vehicle with the bottom sections of the rack bolted to the metal floor of the vehicle. 

The equipment rack will have 12 Volt and 28 Volt equipment mounted on it.

My question.....

- Does a single wire connection from the vehicle's Main Earth Terminal (MET) to the equipment rack meet the protective bonding requirements?

I am hoping that I do not need to have a separate wire from the MET to each individual piece of steel angle, or a 'strap' linking the bolted-joints.


Parents
  • Lost in the rambling mess this forum becomes, the original poster said there isn’t any 240 Vac on the rack, but I’m still unsure if the 12 and 28 volt equipment is AC or D.C.?


    Note - I have just noticed that I didn't mentioned there was 240 Vac in the vehicle. However, there is no 240 Vac equipment or cabling in/on the equipment rack.”

    A full description of the electrical equipment and electrical installations within the vehicle might clarify things, as there seems to be several electrical installations all within the same vehicle, as can happen.

  • Good evening, 

    The 28V and 12V equipment is DC.

    The rack has only 28V DC equipment mounted on it.

    Elsewhere in the vehicle we have various items of equipment that are 240 Vac. 

    All equipment can derive supply from a battery pack mounted on the vehicle (via inverter), or from an external 240 Vac supply that's plugged in to an external connector.

    Steve 

Reply
  • Good evening, 

    The 28V and 12V equipment is DC.

    The rack has only 28V DC equipment mounted on it.

    Elsewhere in the vehicle we have various items of equipment that are 240 Vac. 

    All equipment can derive supply from a battery pack mounted on the vehicle (via inverter), or from an external 240 Vac supply that's plugged in to an external connector.

    Steve 

Children
  • an external 240 Vac supply that's plugged in to an external connector.

    Ah, 'shore power'. That stuffs things quite a bit, and can lead to odd things like shocks between the vehicle and the ground upon which it stands.

    A broken cpc in the shore power tether is a moderately common and credible occurrence, especially on leads that get rolled in and out a lot. So if you have mains equipment (and not much does not) with internal mains filter with comparable capacitance  LE and NE can leave the chassis floating at about half mains voltage relative to terra firma, a nasty surprise for anyone grabbing the door to get in..

    relying on the external supply for earthing can be a bit fraught, and for low power it may be worth considering an isolation TX.

    Be aware that if ever a genset is used there is no  NE bond on many smaller generator designs, and to use conventional ADS methods (RCDS and breakers) an NE bond needs to be added, usually  inside  the 1st plug. However it then needs to be not there when 'plugged in' to a building, or an RCD in that building will see an NE connection as a fault and trip....

    Mike   

  • Hi Mike,

    Good points.

    I think an isolation transformer would be sensible too. Our maximum load is only 3500 Wattts, so transformer size won't be ridiculous.

    I appreciate this doesn't guarantee safety.

    Regards, 

    Steve

    Steve